RE: [10GBASE-T] Technical feasibility: power
Xiaopeng:
 
I 
don't remember anyone demanding nor anyone promising that 1000BASE-T would be 
deliverded at 1 Watt at any stage in developing the standard.  I know of 
multiple initial implementations of 1000BASE-T with higher power 
consumption.  For me personally, the comparison point isn't an arbitrary 
watt number, but is relative to the power consumption of 10 GbE optics 
modules.
 
 
Brad:
 
I 
found no mention of power consumption in the 802.3z critters or objectives, nor 
in the 802.3ab critters or objectives I sampled.
 
· 
Est. Gate Count/Power Consumption: 
330K/4W 
FYI, 
the 802.3ab objectives listed in that presentation were
· 
Comply with specifications for GMII of 
802.3z.
· 
Provide line 
transmission which supports full and half duplex
operation.
· 
Provide FCC Class A/CISPR or better 
operation
· 
Support operation over 
100 meters of Category 5 balanced
cabling
· 
Achieve bit Error Rate better than to 10 
-10
· 
Support Auto-Negotiation (Clause 
28)
· 
Meet susceptibility requirements
· 
Support the objectives of 802.3z of Nov. 13, 
1996
 
--Bob 
Grow
 
I 
believe that the power number would be a big factor in the economic feasibility. 
 If we are talking about a 1 Watt part, then it is not a big deal, but if a 
much higher number turns out, everyone might give a second thought on whether it 
is even worth to implement it.   
Just my thought, 
Xiaopeng 
  
  
    |  | "Booth, Bradley" 
      <bradley.booth@intel.com> 07/31/2003 02:45 PM 
 | To:     
         <xichen@marvell.com>, 
      <stds-802-3-10gbt@ieee.org>
 cc:
 Subject: 
             Re: [10GBASE-T] Technical feasibility: 
      power
 | 
I 
was trying to recall if 802.3 used and specific power numbers in the GbE and 
10GbE objectives or 5 criteria.  Considering I don't have web access right 
now, I'm just going by memory.  I believe 802.3 did not dictate power 
requirements, but did use power estimations in selection of the PHY to put into 
the draft.  This is just a Study Group, so it may only be required that to 
state that due consideration will be given to the power 
requirements.
Thoughts?
Thanks,
Brad
-----------------
Sent 
from my BlackBerry.
-----Original Message-----
From: 
xichen@marvell.com <xichen@marvell.com>
To: stds-802-3-10gbt@ieee.org 
<stds-802-3-10gbt@ieee.org>
Sent: Thu Jul 31 13:52:04 2003
Subject: 
RE: [10GBASE-T] Technical feasibility: power
Burce, 
That is 
what I called painful lessons.  The customers always want parts that have 
high performance margin and low power.  I believe that has become the rule 
for our designers unless you really want something that can also fry eggs. 
 In order to give a reasonable estimation of the power comsuption, we 
should defintely take into account all possible technology and design tricks 
that we know and we can use in 5 years.  Of course, we cannot predict any 
magic stuff that can save the world will come out soon, but we can wait. 
A well-estimated number will save a lot words. 
Xiaopeng 
                
Bruce Tolley <btolley@cisco.com> 
07/31/2003 12:56 PM 
       
       To:     
   xichen@marvell.com, Bruce Tolley <btolley@cisco.com> 
       cc:         
    
   Subject:        RE: [10GBASE-T] Technical 
feasibility: power
Xiaopeng 
Thanks for the 
response
The first 1000BASE-T parts were much more than a few watts. Also 
the power numbers on the roadmaps of the various vendors started dropping as 
soon one of the competitors achieved lower power numbers. All the sudden, the 
impossible became possible.
And yes we need data to be presented in 
September.
Bruce
At 11:10 AM 7/31/2003 -0700, xichen@marvell.com 
wrote:
Hi, 
I believe that everyone of us has painfully learned a 
lot from the history of 1000BASE-T.  We have observed the power of a single 
1000BASE-T dropped from a few watts to sub-watt level today.   And we can 
pretty confidently assess the impact of the technology that we are gonna use in 
5 years and we definitely should take that into account NOW.  
Many 
circuit design experts will tell you that the power of digital circuit part can 
be scaled down while the semiconductor technology got significant improvement in 
the following years (how about using 65nm when 10GB-T reach the market), but the 
analog circuit part won't get too much benefit from that and its performance 
(for example, the ADC resolution) will be limited by some fundamental physical 
rule.  Due to the complexity increase of the DSP part and the analog part, 
even using 65nm technology for digital circuit and using SiGe technology for 
analog circuit, to reach 100m on CAT-7, the estimated power of the transceiver 
(assume it is practically feasible) will be a number that can surprise you. 
 I believe more and more data will be given in the following meeting to 
show you the reality. 
Xiaopeng 
Bruce Tolley 
<btolley@cisco.com> 
Sent by: owner-stds-802-3-10gbt@majordomo.ieee.org 
07/31/2003 10:12 AM 
      
      
To:        pat_thaler@agilent.com, yousefi@broadcom.com, 
pat_thaler@agilent.com, btolley@cisco.com, bradley.booth@intel.com, 
stds-802-3-10gbt@ieee.org 
      cc:       
 
      Subject:        RE: 
[10GBASE-T] September interim meeting 
Pat
Thanks for 
providing detail on data centers. I would argue that in terms of broad market 
potential, 10GBASE-T would pass muster even if the only market application was 
data centers.
On the power issue, the first 1000BASE-T implementations 
did not appear until well after the standard was done, some 5 years after the 
High Speed Study Group got its PAR, and consumed an obscene about of power. We 
might have never achieved the  low power 1000BASE-T PHYs we have today if 
we had tried to agree on exact numbers in 1996. 
Bruce
At 11:00 AM 7/31/2003 -0600, 
pat_thaler@agilent.com wrote: 
Nariman,
CX4 is useful especially when 
we have in rack connections to make or ones going to the next rack. However, the 
distance is too short for many other data center connects. Also, the cable for 
the long distance is relatively bulky which may be a problem for some uses. We 
will be glad to get it, but it only solves a corner of the problem 
space.
Something for the longer distances in data centers that is lower 
cost than fiber would be useful. For that environment, it doesn't necessarily 
have to rely on already installed wiring. Running on existing wiring is nice, 
but not essential.
My view of the important items for the data center 
environment: 
It must perform solidly on the media we choose for it - 
data integrity factors such as BER must be met.
It must be able to live on 
"standard" server bus adapter formats with a TOE: e.g. PCI Express and 
Infiniband
 which means power is a concern
It must be transparent to 
existing MACs - that is, the MAC must see the same behavior it sees with 10 Gig 
fiber.
100 m would be desireable (partly to enable future horizontal usage) 
but the data center could live with shaving something off that. (100 m is nice 
from a standards development standpoint as it saves us from arguing about what 
lower number is enough.)
The media it runs over should not be so stiff or 
bulky that it is a problem to accomodate with normal rack and data center cable 
management.
Of couse it must also meet EMI 
requirements
Regards,
Pat 
-----Original Message----- 
From: 
Nariman Yousefi [ <mailto:yousefi@broadcom.com> 
mailto:yousefi@broadcom.com] 
Sent: Wednesday, July 30, 2003 8:10 PM 
To: 
pat_thaler@agilent.com; btolley@cisco.com; bradley.booth@intel.com; 
stds-802-3-10gbt@ieee.org 
Subject: RE: [10GBASE-T] September interim 
meeting
Pat,
I agree that the issues you raised must be addressed 
by November. One of the biggest challenges for this group is to establish 
reality on technical feasibility on Cat7, Cat6 and Cat5e channels. 
 Different vendors have different conclusion on Technical feasibility. That 
is due to assumptions on alien cross talk mitigation techniques, impact on 
implementation impairments on SNR, channel model, coding gain, and analysis on 
chip complexity in a given process. Assumptions must be stated clearly by 
vendors that present technical feasibility. In this case, technical feasibility 
drives the broad market potential.  Technical feasibility must be addressed 
at least based on the following criteria:
1. Achievable distance on Class 
D channel with and without installation mitigation techniques. 
2. Achievable 
distance on Class E channel with and without installation mitigation techniques. 
3. Transceiver complexity in terms of estimated power dissipation and 
realistic targets for building blocks like ADC, PLL and etc 2-3 years from 
now.
We reached a conclusion that cat7 cable or class F channel has high 
enough capacity for 10Gbps operation.  But, can a transceiver be built with 
reasonable power dissipation and cost say in 90nm process or finer geometries to 
achieve broad market potential? 
We need to keep in mind that customers 
have fiber and CX4 as 
alternatives.
Nariman
At 01:08 PM 
7/30/2003 -0600, pat_thaler@agilent.com wrote: 
Bruce, 
Generally, 
when the group can agree on clear objectives, then they can finish the rest of 
the work. Fuzzy objectives often indicate a lack of real concensus. 
In 
November, I will also be expecting arguments that support the 5 criteria based 
on the objectives - 
especially: 
Broad market potential - evidence that 
there will be a broad market the minimum requirements of the objectives are met. 
Technical feasibility - is it feasible to meet those minimum 
requirements 
Economic feasibility - when you have met the minimum 
requirements will cost be suitable to make it a viable product in the markets? 
In the discussions at the plenary, a power consumption issue was raised 
by some of the speakers. 
If the broad market potential is based in part on 
use in devices such as end nodes (including servers in data centers), then an 
objective for power consumption such that this can reside in server card formats 
would be important. Can it fit within the power constraints of a PCI Express 
board and an Infiniband board (remembering that one has to allow some power for 
the MAC and probably TOE/RDMAP engine)? 
 
Looking at the objectifves 
in agenda_1_07_03, I don't see any that address power consumption or the 
abilitiy to live on server card formats. In a quick search, I also didn't find 
any material on power consumption in the presentations that have been made to 
the study group. I hope that in September the group will address the issue of 
power. 
Regards, 
Pat 
-----Original Message----- 
From: Bruce 
Tolley [ <mailto:btolley@cisco.com> mailto:btolley@cisco.com] 
Sent: 
Monday, July 28, 2003 1:22 PM 
To: Booth, Bradley; stds-802-3-10gbt@ieee.org 
Subject: Re: [10GBASE-T] September interim 
meeting
Brad:
Thanks for the follow up.
I am confident that 
if we can agree on crisp, clear objectives for 10 Gbps reach and media supported 
in September that we can get our PAR approved and move into Task Force mode, 
which is where the real work begins.
Bruce
At 06:35 PM 7/24/2003 -0700, Booth, Bradley 
wrote:
Study Group Members, 
Just to let others that were not at 
the meeting know the outcome of the 802.3 Working Group meeting, the Study Group 
will have to complete its PAR, 5 Criteria and Objectives in November.  This 
gives the Study Group the task of completing the PAR, 5 Criteria and Objectives 
in 4 months.  This will make our September Interim meeting extremely 
important.  We will need to complete the effort as much as possible to 
pre-submit to the 802.3 Working Group prior to the November Plenary. 
 November will permit us the ability to modify the PAR, 5 Criteria and 
Objectives prior to asking 802.3 to put the PAR on the NesCom agenda.  The 
September Interim meeting will focus on the completion of our PAR, 5 Criteria 
and Objectives. 
Thanks, 
Brad 
Chair, 10GBASE-T Study Group 
Bruce Tolley 
Senior Manager, Emerging Technologies 
Gigabit 
Systems Business Unit 
Cisco Systems 
170 West Tasman Drive 
MS SJ B2 
San Jose, CA 95134-1706 
internet: btolley@cisco.com 
ip phone: 
408-526-4534 
"Don't put your hiking boots in the oven unless you plan on 
eating them."
Colin Fletcher, The Complete Walker 
Nariman 
Yousefi
Vice President Networking Engineering
PH  (949) 585 
5450
FAX (949) 453 1848
e-mail : Yousefi@Broadcom.com 
Bruce 
Tolley Senior Manager, Emerging Technologies Gigabit Systems Business Unit Cisco 
Systems 170 West Tasman Drive MS SJ B2 San Jose, CA 95134-1706 internet: 
btolley@cisco.com ip phone: 408-526-4534 
"Don't put your hiking boots in the 
oven unless you plan on eating them." 
Colin Fletcher, The Complete Walker 
Bruce Tolley Senior Manager, Emerging Technologies Gigabit Systems 
Business Unit Cisco Systems 170 West Tasman Drive MS SJ B2 San Jose, CA 
95134-1706 internet: btolley@cisco.com ip phone: 408-526-4534 
"Don't put 
your hiking boots in the oven unless you plan on eating them." 
Colin 
Fletcher, The Complete Walker